EDIT - Found the source - finally.
thank you jrs 87.
I was sent to this site by someone here - but I have lost that link and cannot thank him directly. But thank you for the link - kinda tough reading for an old guy but I did glean some jewels there. I now have less confidence in the AASHTO shear friction model. And this structure may have fell somewhere in a danger zone of reliability even if it did meet those design requirements. See what you think - -
The issue of shear friction in this case may not be so cut and dried as it first seems. The following pieces are from a study of the reliability of AASHTO design for shear friction. It touches on several important things.
I need a statistics guru to help here. Anyone?
First - apparently the target relliability index is 3.5 . That seems to provide a probability of failure of 0.04%. Methinks that means one in 2500 will fail. We have how many bridges in the USA?
pf = failure probability
The probability of failure goes up as the reliability index goes down. Example: “In the latter case, a resistance factor of 0.55 was needed to satisfy the target reliability index of 3.50. The AASHTO LRFD specifications–based resistance factors led to reliability indices of 2.80 (pf equal to 0.3%) “.
Now we are down to one failure in 333 bridges.
Help me here - I am losing confidence rapidly.
Factors which influence this?
The results of the parametric study show that the AASHTO LRFD specifications reliability index values depend on the values of the design variables.
Compressive strength of concrete f�c
For normalweight concrete with fc ' between 41 and 55 MPa (5.9 and 8.0 ksi), the AASHTO LRFD specifications reliability index was 2.75 (below the target reliability index), which is significantly higher than the target reliability index when fc ' is greater than 55 MPa. The reliability indices of Soltani et al.’s model were more consistent than those of the AASHTO LRFD specifications IST model, and averaged around 3.50 for all bins.
So this is a one in 333 bridge except the concrete is 8500 psi and not 8000?
Roughness amplitude of interface R
For the tests with normalweight concrete, the AASHTO LRFD specifications reliability index was 2.70 for a roughness amplitude of interface greater than 3 mm (0.1 in.) and 1.55 for a roughness amplitude of interface less than 3 mm. Thus, the AASHTO LRFD specifications model was 1.74 times more reliable when the interface was roughened compared with smooth interfaces.
Now we are getting downto it - about one in 300if the roughness exceeds 3mm - 1/8" - and probably one on a lot less if roughness is less than 1/8".
Compressive force normal to the shear plane Pc
The AASHTO LRFD specifications reliability indices do not relate to the compressive force normal to the shear plane. The reliability index for tests with normalweight concrete was less than 2.87, with or without the presence of a normal force.
Another reason this is a one in 333 bridge?
Interface reinforcement index ρfy
In the tests with normalweight concrete using Soltani et al.’s model, more interface reinforcement led to higher values of reliability index. The lowest reliability index was 2.62 in the AASHTO LRFD specifications model, when the interface reinforcement index was between 2.8 and 5.5 MPa (0.41 and 0.80 ksi).
Background - -
Per Nowak and Collins12 and Robert,13 the structural reliability or survival probability of structures ps is given by Eq. (10). ps = P(Rm – Q > 0) (10) This is the survival probability of the structural system if the resistance value is more than the load value. Considering Eq. (10), the failure probability pf is determined by Eq. (11). pf = P(Rm – Q < 0) (11) The reliability index β, which is related to the failure probability pf , is defined by Eq. (12). β = –φ–1(pf ) (12) where φ–1() = inverse standard normal distribution function
Calculated the reliability index to be approximately 3.50, which is the target reliability index of most structural design codes, such as the AASHTO LRFD specifications. This target value of 3.50 means that the probability of failure is approximately equal to 0.04%.
The resistance factors of 0.9 (normalweight concrete) and 0.8 (lightweight concrete) in the AASHTO LRFD specifications model led to reliability indices of 2.80 and 5.38 for normalweight and lightweight concrete, respectively. For the tests with normalweight concrete, a resistance factor of 0.55 resulted in the target reliability index of 3.50. The reliability index of the current AASHTO LRFD specifications IST model for normalweight concrete tests is lower than the target reliability index, while the AASHTO LRFD specifications IST model for lightweight concrete is too conservative (no resistance factor needed to satisfy the target reliability index). These results showed the need to revise the AASHTO LRFD specifications IST model and the resistance factors associated with it.
I'm getting the idea bridge engineers do not get paid enough.