Gopher13

Structural
Jun 21, 2016
94
I have a question about the minimum thickness of roof sheathing, and please bear with me, I am self taught on wood design. With reference to the attached tables, it appears as though IBC 2015 limits roof sheathing to 5/8". However, the NDS Supplement diaphragm shear tables only give values up to 19/32" thick? What am I missing? If IBC limits roof sheathing thickness to 5/8", shouldn't the NDS Supplement table start at 5/8" and go up from there (i.e. who cares what the diaphragm shear capacity of 3/8" sheathing if you aren't allowed to use it per IBC)?
 
 http://files.engineering.com/getfile.aspx?folder=dac187dc-657b-47c6-96ee-4c791c1d8529&file=Roof_Sheathing.pdf
Replies continue below

Recommended for you

That table is for decks (lumber). The bottom of that page has a table for plywood.
 