Has anyone any suggestions regarding trying to control an air handler off heating coil temperature when using MTHW at 135degC
Control is very difficult and the temperature tend to over shoot.... its the huge difference between the water temp and the desired air temp is the problem I think.
Air handler is 10m3/s
Air off temperature approx 15 degC.
Im using 2 port control valves.
I've seen installation using pumps to maintain constant volume on the coil...would this help?