EngDM
Structural
- Aug 10, 2021
- 629
I have a bit of a weird case, and I'm hoping someone has put some thought or could provide an outside opinion on the following discussion.
We are retained quite often to design the foundation for a pre-engineered building and act as EOR. This typically involves being provided stamped and sealed reactions by the supplier and running the combinations to size the load path from anchors down to piles. However, there are some instances where we don't get these reactions until way later in design, so we try our best to get a preliminary feel to provide something to the client for pricing. The problem with getting the reactions later is we can't verify their design procedure to try and match.
For a site that is compliant with the requirements of 4.1.8.1.(2) and can be designed with the simplified method, which design rationale would you choose if you had to design a foundation/anchors and lateral system? How do you even begin to choose?
If I start by designing to the simplified method, and the pre-engineered guys designed to equivalent static method for extra ductility to get lighter loads and a more cost-effective structure, does that then require me to satisfy the additional clauses that were otherwise eliminated by 4.1.8.1.(1)? Notably, Table 4.1.8.1.18 has a list of items that need seismic anchoring, that are not mentioned in the simplified method; would I then need to go back and have these miscellaneous structural elements designed for a seismic anchorage?
On the other hand, if I determine loads based on equivalent static, how would I even know what ductility to use without insight into the pre-eng design? If they came back having used simplified method, my preliminary loads would be much smaller.
We are retained quite often to design the foundation for a pre-engineered building and act as EOR. This typically involves being provided stamped and sealed reactions by the supplier and running the combinations to size the load path from anchors down to piles. However, there are some instances where we don't get these reactions until way later in design, so we try our best to get a preliminary feel to provide something to the client for pricing. The problem with getting the reactions later is we can't verify their design procedure to try and match.
For a site that is compliant with the requirements of 4.1.8.1.(2) and can be designed with the simplified method, which design rationale would you choose if you had to design a foundation/anchors and lateral system? How do you even begin to choose?
If I start by designing to the simplified method, and the pre-engineered guys designed to equivalent static method for extra ductility to get lighter loads and a more cost-effective structure, does that then require me to satisfy the additional clauses that were otherwise eliminated by 4.1.8.1.(1)? Notably, Table 4.1.8.1.18 has a list of items that need seismic anchoring, that are not mentioned in the simplified method; would I then need to go back and have these miscellaneous structural elements designed for a seismic anchorage?
On the other hand, if I determine loads based on equivalent static, how would I even know what ductility to use without insight into the pre-eng design? If they came back having used simplified method, my preliminary loads would be much smaller.