tloussaert
Electrical
- Oct 11, 2004
- 2
I have a recent application where I was sizing underground feeders. I sized the feeders according to Table 310.16. My first assessment was that the conductors were either direct burial in encased concrete and they were in metallic conduit in ambient air. About 75% of the run is concrete encased PVC schedule 40 and GRC bends/sweeps, the other 25% is GRC in ambient air. I have used all 4" conduit.
I will be protecting these feeders with a 1600A adjustable trip circuit breaker.
Based on the above facts I selected from Table 310.16 an ampacity rating of 335A for a 400kcmil cable. I chose the 75 Deg C cable rating because the terminals that the cables are being terminated on are rated for 75 Deg C.
If we were to use 6 conductors per phase, we would have a total ampacity of 335Ax6=2010A.
I had figured two conductors per phase in each conduit, this would give us 6 conductors per conduit.
I derated the total ampacity for the number of conductors per conduit 4-6 conductors derate at 80%, from table 310.15(B)(2)(a).
2010Ax0.80=1608A
When I had an independent engineering company review these calculations they informed me that they believe I did not correctly apply the table 310.16 for this application, they feel that I am required to follow the formula listed for 310.15(C), I believe that this formula is an optional calculation to table 310.16. This formula directs the user to Appendix B, I do not believe that this formula is required for underground installations however is unclear. In appendix B it states "This annex is not a part of the requirements of this NFPA document but it is included for informational purposes only."
Could you provide some additional clarification on this subject?
Tom
I will be protecting these feeders with a 1600A adjustable trip circuit breaker.
Based on the above facts I selected from Table 310.16 an ampacity rating of 335A for a 400kcmil cable. I chose the 75 Deg C cable rating because the terminals that the cables are being terminated on are rated for 75 Deg C.
If we were to use 6 conductors per phase, we would have a total ampacity of 335Ax6=2010A.
I had figured two conductors per phase in each conduit, this would give us 6 conductors per conduit.
I derated the total ampacity for the number of conductors per conduit 4-6 conductors derate at 80%, from table 310.15(B)(2)(a).
2010Ax0.80=1608A
When I had an independent engineering company review these calculations they informed me that they believe I did not correctly apply the table 310.16 for this application, they feel that I am required to follow the formula listed for 310.15(C), I believe that this formula is an optional calculation to table 310.16. This formula directs the user to Appendix B, I do not believe that this formula is required for underground installations however is unclear. In appendix B it states "This annex is not a part of the requirements of this NFPA document but it is included for informational purposes only."
Could you provide some additional clarification on this subject?
Tom