notching a PSL post
hapunaterp
Hello -
My question is regarding the analysis or calculations required to determine how notching a PSL post to take a 1 3/4" x 14" LVL beam changes the compression and bending strength of the PSL. Notching a post at the top in order to seat a girder beam is a typical practice but I have always been hesitant to notch a post along its height, say 3' or so from the top and maybe 6' from the bottom (approximately 10'+ tall post). I am cutting out a part of the cross section of the post but I am filling it in with the LVL beam. The question I have, though, is how do I quantify how much this has weakened the post? There will be loads applied vertically (gravity, bearing from beam) and laterally (wind). Thank you very much -
I assume the post is taking load at the top of the post and at the LVL. Is it close to failing if you use the reduced cross-section of the post for the total loads? Maybe try using the reduced section for the loads above the LVL and the full cross-section for the loads below the LVL (with proper eccentricity on the post). Is it a square post? Is the LVL bracing the the strong axis or weak axis?
Using the reduced cross section does not result in failure and the LVL is providing bracing about the weak axis.
Per NDS code, I don't think that you can have a notch in the middle third of a flexural member. I'm not even sure that disregarding the width of the notch would suffice as it's a stress concentration / fracture mechanics thing.
What KootK said, that's a stress concentration and it takes no consideration if they accidentally over cut a bit or otherwise made the notch worse.
I've only notched posts for beam seats at the top of the post away from bending stresses.
Maine Professional and Structural Engineer.