OHGW - overhead ground wire on a transmission tower: want to ask if this GROUND conductor (which is installed at the highest position of the transmission tower) should be a BARE conductor or JACKETED conductor.... I thought : IN CASE OF LIGHTNING STRIKE, the bare conductor completes the circuit to GROUND. thank you.
 
Replies continue below

Recommended for you

You have reasoned it out correctly; jacketed would be a pointless waste of money and defeat the purpose of readily conducting lightning strikes to ground.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
For lightning protection with shield wire utility use bare OHSW or OPGW (Optical Grownd