nickypaliwal
Materials
- Aug 28, 2014
- 199
There is a 18" 10.3mm thick API 5L X65 HFW pipeline which passed all the tests including hydro test in mill however there is a pin hole leak observed near the seam weld which was observed in field hydrotest.
It was difficult to find the location of the leak as the leak is small and was not even detected during full UT.
Many other areas are showing pressure drop however the location is still untraced.
As I read on internet, it looks probably cold weld/penetrator defect.
Is there a way out to confirm if the failure is penetrator defect and what should be the corrective action?
It was difficult to find the location of the leak as the leak is small and was not even detected during full UT.
Many other areas are showing pressure drop however the location is still untraced.
As I read on internet, it looks probably cold weld/penetrator defect.
Is there a way out to confirm if the failure is penetrator defect and what should be the corrective action?