Is any one aware of, or sees an advantage in placing PTs within breaker bays (between the circuit breaker and disconnect) instead of on the outgoing line positions?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
David Beach said:Then there's the question of how do you lose a VT primary without tripping the bus or line it is connected to?
I guess you might get an open, but anything nasty happening to one VT primary would render any other VT on the bus or line temporarily unavailable. It seems to me that a second, fully redundant, VT adds a lot of expense, space, and complexity for a fairly small gain in redundancy.
davidbeach said:We lose VT fuses much more often than we lose VTs, so separate secondaries are far more redundant than one secondary daisy chained between relays.
David Beach said:Sure, I still see a significant common-mode failure risk of taking out both voltages; that's why we turn on overcurrent based protection during LOP conditions. Given that ability to provide alternate protection, I'd much rather push hard on dual batteries and dual trip coils than for a second VT. I know you'd like us to buy twice as many, but that do well enough that other non-redundancies are much more pressing.