Hi,
I'm hoping someone will be able to help me out, as I'm really struggling to understand an issue at work.
We have a fryer with two extract fans which worked fine previously. But as they were very old we decided to overhaul all the ducting and fans, and also they were galv so we couldn't keep them too clean, and they leaked oil.
We replaced the pipe work, and made everything straight, and bought two new bifurcated fans, everything made from stainless steel.
I asked the manufacturer of the fryer what m3/h each new fan should be rated at, to which I was told 300m3/h per fan is what they normally install and is more than enough. So I ordered 2-off new fans at £900 each, and had everything fitted.
Unfortunately the fans do not extract what they should and it makes the room full of smoke after a short while. At the time of ordering the fans I didn't specify any Pressures, as I don't have a clue about what they should have been (or that I needed to), just the 300m3/h per fan. The company selling the fans didn't state or ask anything either!
The new fans have a Pressure rating of 70Pa, which from a bit of reading shows this is hardly anything! We have fat filters on the outlet of the ducting, which I believe have a pressure drop of 200Pa in them!
Can anyone please help me in estimating what the pressure rating of the fans at 300m3/h should be with the following:
- Fat filter: 200Pa (awaiting confirmation from manufacturer)
- 200mm diameter stainless steel pipe work, straight, total 5m
- Ducting cowling at the top (Jet Cap) - ?Pa (awaiting confirmation from manufacturer)
I think we are going to have to spend even more money buying new fans now, as the company said it was my fault for specifying 70Pa pressure for the fans, although I didn’t, but I accept I was inexperienced in purchasing new fans, thinking all I needed to ask for was stainless steel fans with a rating of 300m3/h.
But in what application could a 300m3/h fan be used at 70Pa pressure? As I think even short runs of pipe work would result in a higher pressure loss then 70Pa?
Thanks a lot
Ryan
I'm hoping someone will be able to help me out, as I'm really struggling to understand an issue at work.
We have a fryer with two extract fans which worked fine previously. But as they were very old we decided to overhaul all the ducting and fans, and also they were galv so we couldn't keep them too clean, and they leaked oil.
We replaced the pipe work, and made everything straight, and bought two new bifurcated fans, everything made from stainless steel.
I asked the manufacturer of the fryer what m3/h each new fan should be rated at, to which I was told 300m3/h per fan is what they normally install and is more than enough. So I ordered 2-off new fans at £900 each, and had everything fitted.
Unfortunately the fans do not extract what they should and it makes the room full of smoke after a short while. At the time of ordering the fans I didn't specify any Pressures, as I don't have a clue about what they should have been (or that I needed to), just the 300m3/h per fan. The company selling the fans didn't state or ask anything either!
The new fans have a Pressure rating of 70Pa, which from a bit of reading shows this is hardly anything! We have fat filters on the outlet of the ducting, which I believe have a pressure drop of 200Pa in them!
Can anyone please help me in estimating what the pressure rating of the fans at 300m3/h should be with the following:
- Fat filter: 200Pa (awaiting confirmation from manufacturer)
- 200mm diameter stainless steel pipe work, straight, total 5m
- Ducting cowling at the top (Jet Cap) - ?Pa (awaiting confirmation from manufacturer)
I think we are going to have to spend even more money buying new fans now, as the company said it was my fault for specifying 70Pa pressure for the fans, although I didn’t, but I accept I was inexperienced in purchasing new fans, thinking all I needed to ask for was stainless steel fans with a rating of 300m3/h.
But in what application could a 300m3/h fan be used at 70Pa pressure? As I think even short runs of pipe work would result in a higher pressure loss then 70Pa?
Thanks a lot
Ryan