This issue came up in the truss forum (not one of my posts, but I did chime in), but it's been dead for a bit with no real resolution, so I'd like to get some opinions here.
In the case of a truss (scissor or otherwise, but especially scissor trusses), if the truss is designed as simple-simple, the bottom chord is in tension and one end (or both) would move horizontally even if just a bit.
If you know, for example, that the horizontal movement of one end of the truss is going to be 1/2" per the fabricator, I think you need to actually allow for the movement and NOT try to eliminate it without having the truss fabricator redesign the truss.
Here is my reasoning. If the truss is designed to allow horizontal movement of one end of the truss, the bottom chord will be in tension only. As you start to restrict that movement by introducing a beam at the top of the wall (or whatever other method you choose) the bottom chord will end up going into compression as it tries to displace horizontally and is restricted. Now a truss chord that was designed for tension is taking compressive loads and this is definitely not a good thing.
I would think that you either:
1. Need to tell the fabricator up front that horizontal displacement of either end of the truss will not be permitted to allow him to design it properly.
2. Allow for the displacement the fabricator tells you to expect.
I just think that being told to expect 1/2" horizontal movement and then trying to restrict it is a bad idea.
Any opinions.
In the case of a truss (scissor or otherwise, but especially scissor trusses), if the truss is designed as simple-simple, the bottom chord is in tension and one end (or both) would move horizontally even if just a bit.
If you know, for example, that the horizontal movement of one end of the truss is going to be 1/2" per the fabricator, I think you need to actually allow for the movement and NOT try to eliminate it without having the truss fabricator redesign the truss.
Here is my reasoning. If the truss is designed to allow horizontal movement of one end of the truss, the bottom chord will be in tension only. As you start to restrict that movement by introducing a beam at the top of the wall (or whatever other method you choose) the bottom chord will end up going into compression as it tries to displace horizontally and is restricted. Now a truss chord that was designed for tension is taking compressive loads and this is definitely not a good thing.
I would think that you either:
1. Need to tell the fabricator up front that horizontal displacement of either end of the truss will not be permitted to allow him to design it properly.
2. Allow for the displacement the fabricator tells you to expect.
I just think that being told to expect 1/2" horizontal movement and then trying to restrict it is a bad idea.
Any opinions.