pattiane

Electrical
Apr 24, 2006
19
Hi all,

I am struggling with PI controller to control a curretn controller.The control is in discrete time.

Basically, i have a set-up with an inverter and LCL filter.
The idea is to control, using dSPACE, the current in d and q axis measured in the output of the LCL filter.

What I'm currently doing is to use a model of LCL filter to tune my PI regulator in Simulink.The reference current is a step.
The model of LCL filter is good, there is no problem.
My simulation model is also right, I checked with an other sample of LCL parameters.

But with my set-up of LCL filter, I cannt reduce the resulted overshoot .

I don't know if you get my point...
Basically, I need to know why in certain systems we cannot reduce the overshoot, is it because of a wrong compensation of poles?...

Thanks
 
Replies continue below

Recommended for you

Hello skogsgurra,

About Rd in not working system,it is high.
Actually, this damping resistor is calculated theoritically by taking into account resonance frequency and capacitor:
Rd= 1/3 * 1/ (OMEGA_res.C)
But it is true that in real, it should be very small about mOhm. But I wanted to check firstly with the theoritical value.
 
Hi All,

Yes, it is Skogsgurra.
Ive resolved my problem yersteday...

The source of problem was the used design of PI controller.
I didn't use a normal controller, the design was slight different.
Once tuned the PI using SISOTOOL(Simulink GUI), Ive taken the transfer function of PI from that, with
Kp (z-zp)/(z-1) format.
Since the discretization of the controller is done by Tustin method in SISOTOOL, zp= (Tsw-2Ti)/(Tsw+2Ti), I can find out Ti knowing the switching period Tsw.

"A PI controller can only be used to place one pole since the integrator has its own pole."PNachtwey
I forgot to mention also that the capacitor C of LCL filter can be negligible.
why? Because, C is DELTA wired in 3-phases, then in Y wired configuration, the current passing through C is equal to :
Ic = Vphase to neutral / Zc
with Zc= 9.6 uF * (2*pi*50Hz)
Ic is about 0.7 A, so the capacitor can be negligible, then
the transfert function of the plant (LCL) becomes:
H(s)= 1 / (Li+Lg)s
1 pole instead of 3 poles, you can check it works, the control is the same.

Thanks anyway for your help and questions.

LP
 
You got me confused there. And I still am. Difference equations (z) are perhaps more common in pure DSP programming. Control people are used to s domain.



Gunnar Englund
 
Skogsgurra,

Ok, let's say that I was able to tune the controller using SISOtool, which enables to find pole and zero of the controller.
In PI case:
Kp (1+ Ki/s) = K( s + Ki) / s with Ki=1/Ti
Ki is the zero of the plant.

So I was to find Ki and Kp via SISOtool.That's all.



 
The problem was from the design of PI with Simulink blocks.
But I still don't understand why this design works with the first set-up and not with the second set-up, which is mine.

In fact,using PI as a transfer function has resolved the problem, in my global system.



 