When designing key elements for an applied load of 34kN/m2 (such as corner columns on a high-rise) as a way to satisfy robustness and avoid disproportionate collapse, what effective column length do you consider? Is it acceptable to check the column capacity based on a single story height, or do you ignore the lateral restraint offered by the slab? If the slab is ignored, over how many levels do you disregard the restraining effect of the slab?
With reference to the IStructE document - Practical Guide to Structural Robustness & Disproportionate Collapse in Buildings", we have the following extract:
"The general design approach for key elements is to consider uniform pressure acting over their surface (in each orthogonal direction, one direction at a time) plus the surface of any attached items such as cladding. Likewise, any member restraining a key element should be designed for the specified design pressure or the restraining element benefits ignored. The restraining element can be checked separately to the key element however, if both would be affected by the same event, then it is more logical to consider both elements loaded simultaneously. The pressure is applied in conjunction with the accidental load case"
"It would be unduly onerous to apply the accidental design pressure over large areas, e.g. to slabs attached to (and stabilising) long span transfer beams...so applying the pressure to an area limited to 6m × 6m would seem reasonable, although any such relaxation should be considered in light of the specific circumstances."
With reference to the IStructE document - Practical Guide to Structural Robustness & Disproportionate Collapse in Buildings", we have the following extract:
"The general design approach for key elements is to consider uniform pressure acting over their surface (in each orthogonal direction, one direction at a time) plus the surface of any attached items such as cladding. Likewise, any member restraining a key element should be designed for the specified design pressure or the restraining element benefits ignored. The restraining element can be checked separately to the key element however, if both would be affected by the same event, then it is more logical to consider both elements loaded simultaneously. The pressure is applied in conjunction with the accidental load case"
"It would be unduly onerous to apply the accidental design pressure over large areas, e.g. to slabs attached to (and stabilising) long span transfer beams...so applying the pressure to an area limited to 6m × 6m would seem reasonable, although any such relaxation should be considered in light of the specific circumstances."