I would like to know how do you guys set the safety clearance for the following type;

i. Minimum horizontal safety clearance from the nearest conductor
ii. Insulation Requirement - Rated short duration power frequency withstand voltage
a. phase - Earth and between phase;
b. across open switching device and/or isolating distance;

according to 275 kV Substation, the following answer are
i. 3900mm
ii. a. 395 kV
b. 425 kV

I would like to know 132 kV and method to calculate or any standards related to them ?

Regards,
Linspire
 
Replies continue below

Recommended for you

Safety clearances tend to be country specific depending on legislative requirements, Company or industry standards, safety rules and procedures. Which country are you concerned with?
Regards
Marmite
 
I can’t open the attachment. From Australian standard AS 2067 and IEC 60694 there are the results:
Minimum horizontal safety clearance from the nearest conductor : AS2067 Table 1 275[300] KV 3914mm 132[145] KV 3330 mm
ii. Insulation Requirement - Rated short duration power frequency withstand voltage : IEC 60694 Table 2a 300[275]KV ; 145[132] KV Table 1a
a. phase - Earth and between phase: 380 KV ; 275 KV
b. across open switching device and/or isolating distance : 435 KV ;315 kV
 