Hi everyone,
In the Wood Design Manual there's a factor Kzc which is used to determine compressive capacity of sawn timber columns. The equation is as follows:
Kzc = 6.3(dL)^-0.13 <= 1.3 or Kzc = 6.3(bL)^-0.13 <= 1.3 which ever is more
This factor is to account for the size of the member to check for buckling in both axis of the member.
The thing that is confusing for me is that if the factor exceeds 1.3, intuitively I would decrease my member length, but this makes the factor larger do to the negative exponent.
For example,
Using a 14ft (4268 mm) 2 x 6; b=38 mm, d=140 mm
Kzc = 6.3(38x4268)^-0.13 = 1.32 > 1.3 NG
So if I lessen the member length to 4000 mm
Kzc = 1.335
Is this right?
In the Wood Design Manual there's a factor Kzc which is used to determine compressive capacity of sawn timber columns. The equation is as follows:
Kzc = 6.3(dL)^-0.13 <= 1.3 or Kzc = 6.3(bL)^-0.13 <= 1.3 which ever is more
This factor is to account for the size of the member to check for buckling in both axis of the member.
The thing that is confusing for me is that if the factor exceeds 1.3, intuitively I would decrease my member length, but this makes the factor larger do to the negative exponent.
For example,
Using a 14ft (4268 mm) 2 x 6; b=38 mm, d=140 mm
Kzc = 6.3(38x4268)^-0.13 = 1.32 > 1.3 NG
So if I lessen the member length to 4000 mm
Kzc = 1.335
Is this right?