hamza41

Civil/Environmental
Jul 7, 2015
51
Hello,

I'd like to check the stability of RC columns against the reactions of a space frame. The columns' height is 12 m and their diameter is 60 cm. The issue is to decide the effective length factor value to adopt for this case to determine the critical buckling load P[sub]c[/sub].
At first sight, the structure is sway as no bracing elements are present.
The question is: can I consider my structure as nonsway if it complies with the following condition (10-10) of ACI 318-11 and adopt an effective length factor of 1 instead of 2, or is this conditon only available for the determination of the Moment magnification procedure ?

Thank you.

SF_xqo8gw.jpg

ACI_erqevh.jpg
 
Replies continue below

Recommended for you

Is that horizontal reaction from gravity loading only? You need to consider also wind loading, and volume change in the steel structure due to temperature variation.
 
This is the factored reaction from dead and wind loads on the roof.
I will check reactions from temperature load too. It shall be limited to almost 30 % of vertical reactions by the adoption of sliding supports.
 
The maximum horizontal reaction for temperature variation load of 30° is 2.63 KN.
I think we don't need sliding supports, it'd be useless.
 