Testing a Vacuum Breather Valve

Status
Not open for further replies.

Inchtain

Petroleum
Feb 21, 2021
132
Dear colleagues,

We have a Vaccum Breather Valve whose setting is -10 mbar and installed at a fuel gas blanketed Water Backwash Clarifier (The design pressure of the Vessel is 20 mbar and the current vessel operating pressure is 5 mbar; while the diameter of the vessel is 3600 mm and the height is 7000 mm with a thickness of 14mm bottom head/10 mm shell and top head)

When testing the setting of this vaccum breather valve and after lapping the seat and replacing the diaphram, the valve fully opens at -9.3 mbar with no leaking when it is closed, so do you think that we can accept the test and install back the valve?

Thanks.
 
Replies continue below

Recommended for you

Tank Breather valve set pressure tolerance is +-10%. As mentioned above, if the valve opens at -9.3, it is acceptable.
 