hollerg
Chemical
- Mar 22, 1999
- 97
I have an ASME code vessel running 85% liquid full, which fire exposure would result in the PRD lifting. The material would be just below the pseudocritical condition during the relief. Downstream there is and an undersized flare, when I compute the valve size by API-521 with the minimum insulation credit. It’s a 4000 gallon vessel with adequate drainage. The valve is grossly oversized, by API-521 with the minimum insulation credit. Depressurization rate would be too high for the flare.
Although I can mitigate the required flow and could downsize the valve by additional insulation, it’s not enough to impact the fire case load from the fire pool. However, if I can insulate and make fire a non credible scenario & not get the wall hot enough to need depressurization, then the existing valve can stay and the flare system meets requirements.
1. Is it appropriate to insulate sufficiently that the insulation prevents a fire driven release for what is declared to be beyond a “reasonable” fire duration? E.G.
a. Assume -- Proper installation of sufficient insulation
b. Assume – HAZOP review agrees that the fire would extinguish before the PRD would lift
…. then does Fire Case become a non-credible scenario, and the PRD would be sized to meet any remaining credible scenario?
2. IF there were no other credible scenario, then could the PRD be completely omitted?
3. Is the method in the spreadsheet an adequate estimate of the time to relief?
4. Do I need to perform another calculation to examine the wall temperature criteria, or is it safe to assume the wall temperature is the same as the temperature when the PRD is ready to POP?
Although I can mitigate the required flow and could downsize the valve by additional insulation, it’s not enough to impact the fire case load from the fire pool. However, if I can insulate and make fire a non credible scenario & not get the wall hot enough to need depressurization, then the existing valve can stay and the flare system meets requirements.
1. Is it appropriate to insulate sufficiently that the insulation prevents a fire driven release for what is declared to be beyond a “reasonable” fire duration? E.G.
a. Assume -- Proper installation of sufficient insulation
b. Assume – HAZOP review agrees that the fire would extinguish before the PRD would lift
…. then does Fire Case become a non-credible scenario, and the PRD would be sized to meet any remaining credible scenario?
2. IF there were no other credible scenario, then could the PRD be completely omitted?
3. Is the method in the spreadsheet an adequate estimate of the time to relief?
4. Do I need to perform another calculation to examine the wall temperature criteria, or is it safe to assume the wall temperature is the same as the temperature when the PRD is ready to POP?