This would be again considering 0.1 microsecond rise time pulses in a power system. There are two different types of concern:
1 - surges from power system propogating toward the motor.. we'd like to lessen them.
2 - surges generated by partial discharge inside the motor which propogate outward into terminal box, make a right angle turn to get to coupling capacitor filter network for sending partial discharge.
In both cases, there is occasions where the surge may encounter a 90 degree turn in the copper buswork within the terminal box. I'm guessing the buswork is 1/4" thick.
What effect does a 90 degree turn have on pulses that I assume are initially propogating in transverse electromagnetic mode.
What about a 90 degree tap. i.e. surge has the choice to go straight or make a 90 degree turn... will any of it go down the 90 degree tap>?
=====================================
(2B)+(2B)' ?
1 - surges from power system propogating toward the motor.. we'd like to lessen them.
2 - surges generated by partial discharge inside the motor which propogate outward into terminal box, make a right angle turn to get to coupling capacitor filter network for sending partial discharge.
In both cases, there is occasions where the surge may encounter a 90 degree turn in the copper buswork within the terminal box. I'm guessing the buswork is 1/4" thick.
What effect does a 90 degree turn have on pulses that I assume are initially propogating in transverse electromagnetic mode.
What about a 90 degree tap. i.e. surge has the choice to go straight or make a 90 degree turn... will any of it go down the 90 degree tap>?
=====================================
(2B)+(2B)' ?