-
1
- #1
Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Transformer explosion and fire:
Looks like there was sustained arcing on the secondary before the explosion:
I'm guessing a short circuit occurred on the 12kv (or 16kv) side with relaying failing to catch/clear it. The transformer remained severally overloaded overheating to the point the oil inside it ignited.
I don't take credit for these picture but to give you an idea that power transformers typically contain anywhere between 7,000 to very well over 25,000 gallons of oil.
Can I make the claim that my practice of 200E fuses on the primary would have prevented all this?
Looks like there was sustained arcing on the secondary before the explosion:
I'm guessing a short circuit occurred on the 12kv (or 16kv) side with relaying failing to catch/clear it. The transformer remained severally overloaded overheating to the point the oil inside it ignited.
I don't take credit for these picture but to give you an idea that power transformers typically contain anywhere between 7,000 to very well over 25,000 gallons of oil.
Can I make the claim that my practice of 200E fuses on the primary would have prevented all this?