You’re asking us to provide a standalone document when there are hundreds of standards spread across lots of disciplines. You’re going to need to be more specific
Hello,
We have typically been designing large scale PV plants with Y-D-Y GSU's with a NGR on X0. Why not use a Y-D transformer and use novel methods of detecting ground faults (3V0)? I understand that you would need to do a more in depth insulation study because of the larger neutral shift and...
not really much you can do about step potentials at the periphery other than spending needless money to lower the overall GPR below the tolerated step potential.
We wire test switches on both positive and negative side of the relay output contacts only. You don't want to wire a test switch directly inline to the breaker trip coils for obvious reasons. Any testing of the breaker trip circuit needs to be done when the breaker is isolated from the system.
Hi Davidbeach,
I understand maintenance mode settings drop the instantaneous setting low temporarily. I was referring to the af levels during normal operation.
I agree with other sentiments that the engineer should provide justification for the setting values. I think it’s worth noting that the instantaneous element of a relay usually isn’t used for mitigating arc flash, but more for protecting equipment from serious damage. Arcing current *usually*...
I assume you’re referring to the amount of traverses for a site. I’ve only seen 2 traverses conducted at different sites, but I could imagine if a site contained a discontinuous soil makeup, more traverses would be a good idea.
I don't think sticking a single line diagram in ETAP (or any computer aided design and analysis program for that matter) will get you very far in learning about electrical power components. If you happen to select the correct component, you would need to then add necessary parameters. This...