Attached are links to the Expert hearings & reports. There are a total so far, of 3 Expert Hearings & 4 Expert Reports.
I have watched two of the hearings 3 to 4 hours each.
Dr Barbara Lane's presentation: Part 1 of the video covers Building Standards & Grenfell's building history, while part 2 applies the standards to the work done to Grenfell.
Professor Luke Bisby's expert report, also in two parts. In part 1 discusses fire generation & methods of evaluation material combustion, while part 2 applies what was discussed in part 1 to Grenfell; much as did Dr Barbara Lane. You could skip part one of both of these, although they make good classroom material on the subjects covered.
The links also contain a link to a pdf of the report. I recommend the pdf. They are definitely worth a look and contain many "As Built" and detailed post fire photos.
To add some clarity to the reports of polystyrene in the facade, it appears the Window In-fill Panels & the Fan Opening Insert were an ACM material (Aluglaze)
Link made up of 2ea - 2mm sheets of aluminum & 25mm of polystyrene. Many of these Aluminum In-fill sheets fell from Grenfell during the fire. One suspicion is that the fan may have fallen out of this panel during the initial kitchen fire & the fan opening was the earliest route of flame to the exterior.
Comparing Dr Barbara Lane's determination of where Fire Block SHOULD have been and where fire block was placed, just over half as much was used as standards require and though detailed; was missing in vertical positions on a number of the columns.
No form of fire-stopping was found in any of the window assemblies, where the window stopped short of the column. The only consideration was for waterproofing the gap with an EPDM membrane and additional insulation board. Forensic deconstruction frequently found the insulation had been omitted. The interior of the gap was filled with a 10mm strip of uPVC that started to lose strength at about 50C. This same uPVC was used in the interior window surrounds and one of the reports show a photo from a partially damaged apartment with the uPVC in a frozen state of melting.
Professor Luke Bisby speaks a great deal to the rapid vertical advancement of the fire, followed by the melting, downward & horizontal envelopment. His link has a compilation video that gives a time position to the many video and show the advancement of the fire from very early in the fire to full conflagration.
Looking at Professor Niamh Nic Daeid's report it becomes clear that by the time the fire crew in unit 16 finally started to apply water to the kitchen blaze, the facade had been ignited for 1 or 2 minutes.
(scroll the link for pdf)