Does anyone know the 30*C AC resistance (or impedance) of 14, 12 and 10 gauge wire?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Fischstabchen said:The difference between 75C and 30C is only going to be less than 2%.
Proposing this change be made to 250.4 (A) 5, and that a new paragraph 250.4 (A) 6 be added after 250.4 (A) 5.
(5) Effective Ground-Fault Current Path. Electrical equipment
and wiring and other electrically conductive material
likely to become energized shall be installed in a manner that
creates a low-impedance circuit facilitating the operation of the
overcurrent device not exceeding the time specified in 250.4 (A) 6 or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path.
(6) Maximum Permitted Overcurrent Device Disconnection Time. The maximum total clearing time of an associated overcurrent device during a ground fault shall not exceed any of the following:
(a) 1 second for final branch circuits protected at 30 amps or less, operating over 50 volts to ground but not exceeding 150 volts to ground.
(b) 0.5 seconds for final branch circuits protected at 30 amps amps or less, operating over 150 volts to ground but not exceeding 300 volts to ground.
(c) 0.25 seconds for final branch circuits protected at 30 amps or less, operating over 300 volts to ground but not exceeding 600 volts to ground.
(d) 0.125 seconds for final branch circuits protected at 30 amps or less, operating at over 600 volts to ground.
(e) 5 seconds for feeders and branch circuits protected at 35 amps or more but not exceeding 350 amps, operating at over 50 volts to ground.
(f) 10 seconds for feeders and branch circuits protected at 400 amps or more, operating over 50 volts to ground.
FPN: Disconnection time is typically derived via
the minimum fault current as determined by the total
combined circuit impedance present at the furthest
point of a circuit's fixed wiring compared to a device's
published time current curve. See Chapter 9, Table 9
for specific impedance values.
FPN: Faster disconnection times than maximum
limits above greatly reduce incident energy
at the point of a ground fault.