Hi, All
I just read the 12 or so, different post about soft starters, and I have a different question reguarding the use of these devices.
We have installed several SMC soft starters over the past six months. They are on a 25 HP motor, 480 volts 3 PH. The 480 volt power system is an ungrounded system. IE the unit sub is a 2500 KVA delta - delta transformer. They had been running OK for several months. The motor FLA is 31, but the normal running load is only about 12 amps. Very lightly loaded.
Last week, we had several of the soft starters shut down, within seconds of each other. We noticed, that at about the same time we had a single phase ground, coming and going. Several hits every few seconds, lasting for up to 20 min.
When we looked at the phase to ground voltages, using a Dranetz analyzer, we see transients up to 900 volts, when these grounds occure. Apparently the soft starters don't like the "Noise" on the line, and shut down.
My plan is to install a 3 PH contactor in parallel with the soft starter, and have it by pass the soft starter aftr the motor is up to speed.
Question, do I need to size the by pass contactor, based on the motor HP, or can I use a smaller unit, sense it will only see runing current and not starting currents?
The soft starter unit itself, has 3 small relay contacts, used to by pass the SCR's, after the motor gets up to speed.
The bypass contactor will be used to disconnect the motor from the line when the motor is stopped, and / or when the motor overloads take the motor off line.
Thanks for your response.
I just read the 12 or so, different post about soft starters, and I have a different question reguarding the use of these devices.
We have installed several SMC soft starters over the past six months. They are on a 25 HP motor, 480 volts 3 PH. The 480 volt power system is an ungrounded system. IE the unit sub is a 2500 KVA delta - delta transformer. They had been running OK for several months. The motor FLA is 31, but the normal running load is only about 12 amps. Very lightly loaded.
Last week, we had several of the soft starters shut down, within seconds of each other. We noticed, that at about the same time we had a single phase ground, coming and going. Several hits every few seconds, lasting for up to 20 min.
When we looked at the phase to ground voltages, using a Dranetz analyzer, we see transients up to 900 volts, when these grounds occure. Apparently the soft starters don't like the "Noise" on the line, and shut down.
My plan is to install a 3 PH contactor in parallel with the soft starter, and have it by pass the soft starter aftr the motor is up to speed.
Question, do I need to size the by pass contactor, based on the motor HP, or can I use a smaller unit, sense it will only see runing current and not starting currents?
The soft starter unit itself, has 3 small relay contacts, used to by pass the SCR's, after the motor gets up to speed.
The bypass contactor will be used to disconnect the motor from the line when the motor is stopped, and / or when the motor overloads take the motor off line.
Thanks for your response.