tmac7285
Structural
- Dec 22, 2019
- 19
The 1170.4 clause 1.1 (g) states that buildings with a first mode period greater than 5 seconds is outside the scope of the standard. Where or whom are we supposed to go to for this approach?
1170.2 has a similar criterion and that the code based wind does not include any buildings with a period greater than 5 seconds, amongst other criteria. It's clear that we should consult a wind engineer and get the building tested in a wind tunnel. This is not so clear for earthquake.
Is the aforementioned 1170.4 clause essentially not representative of the taller structures we are building now? Can this clause be ignored if we undertake a rigorous analysis?
1170.2 has a similar criterion and that the code based wind does not include any buildings with a period greater than 5 seconds, amongst other criteria. It's clear that we should consult a wind engineer and get the building tested in a wind tunnel. This is not so clear for earthquake.
Is the aforementioned 1170.4 clause essentially not representative of the taller structures we are building now? Can this clause be ignored if we undertake a rigorous analysis?