LionelHutz (Electrical) said:Using an undervoltage release on the circuit breaker seems odd.
LionelHutz (Electrical) said:UVR is not common in any kind of industrial environment. We have about 30 MV breakers on the shelves right now and none have UVR coils in them. ...You get full control over tripping of breakers by using protection relays and trip coils, hence why that's the dominant control scheme employed.
NTSB said:NTSB investigators (in coordination with vessel crew and parties to the investigation) noted an interruption in the control circuit for HR1’s undervoltage release.[1]Link