CDTP for Fulflo valve

Status
Not open for further replies.

Nasim12345

Industrial
Apr 25, 2017
53
Dear Sir
I need your advice to calculate the CDTP(Cold Differential Test Pressure) for the Fulflo valve. Pls refer the attached data sheet.

Set pressure is 7.03 Kg/cm2D (differential pressure)
Constant superimposed back pressure is 18.47 Kg/cm2g
Can you pls advice the CDTP? Is it 7.03 Kg/mc2g?
Data_Sheet_elad8v.png

Cold Differential Test Pressure (CDTP)
The cold differential set or test pressure is the actual pressure at which the valve will open on a test stand. As PZVs are usually set and tested at ambient temperature with no backpressure, the CDTP includes any necessary correction for the actual application, based upon backpressure and / or temperature. Backpressure correction is only needed for Conventional PZVs and it addresses constant backpressure only.
CDTP (Conventional PZV) = (Set Pressure – Constant Superimposed Back Pressure) * Temperature Correction Factor.
CDTP (Bellows or Pilot PZV) = Set Pressure * Temperature Correction Factor.
The Pressure adjustment for temperature is specific to the Manufacturer and PZV Model. Consult the manufacturer for discharge temperatures above 150°F.





Thanks
Nasim
 
Replies continue below

Recommended for you

gg That's an out of date API-520 See above.

Per ISO-4126, only the term Safety Valve is used regardless of application or design.
 
Sometimes I think there should be some sort of commission related to contribution, Lol.
 