So I've been studying ACI 318-08 App D all day on this particular situation. No examples to be found as I search and search for a concrete column with embed plates. As I understand I need to check Vcbg, but I get to multiply by 2 (Per D6.2.1(c)) since the only load is the 120k Shear load (LRFD level) is parallel to the nearest edge. That yields only about 30ish kips of allowable load for quite a robust embed plate. Now, I can of course use the D6.2.9 anchor reinforcement, but I can't really fathom what the failure plane would be for a column embed like this, thus I don't know what rebar to develop.
To me Vcbg doesn't make sense for a column like this. Pryout check makes sense (but even then stirrups help prevent that), and when I check that I get 127.5 kips of capacity.
Anyone encountered this before and have thoughts?