design of ladder stiles 2
When you say "stile", I picture something like the attached, which seems to be different from what you're doing. So what exactly are you designing?
I've seen the 'side rails' referred to as 'stiles.. not often, but has happened. I don't know if 'side rails' is the correct term.
From my Project Notes:
-DESIGN LOADING:
DL AND LL FACTORS FOR LADDERS, AND GUARDS BOTH ASSUMED TO BE 1.0;
RUNGS AND ACCESS STAIRS 1.32KN (300LB) AT ANY LOCATION EACH 10’ OF HEIGHT IN ACCORDANCE WITH ASCE 7;
1.2KN (250LB) AT ANY LOCATION ON ANY TWO ADJACENT RUNGS IN ACCORD WITH ANSI A14.3;
LADDER RAILS 4.448KN (1000LB) VERTICAL AT ANY LOCATION;
LADDER LOAD IS SHARED BY 4 FASTENERS;
LADDER DEAD LOAD SHALL BE LESS THAN 75 LBS PER FASTENER;
LADDER RAILING AT TOP IS NOT DESIGNED AS A GUARD; AND
LADDER RUNGS SHALL BE NON-SLIP.
-HEIGHT OF LADDER MARGINALLY EXCEEDS 5 M. A VARIANCE SHOULD BE OBTAINED FROM THE AHJ TO PERMIT ACCEPTANCE.
-SUPPLY AND INSTALL BILCO LADDER UP SAFETY POST MODEL LU-4 ALUMINUM OR APP’D EQ
The arrow shows what i am designing in the ladder
dik,
I'm not familiar with the ANSI A14.3 - what's the purpose of the (2) 250 pound loads on adjacent rungs? Are those loads vertical only, or are they a moment couple?
I'm not sure... just to provide an extreme overloading? You would think the agencies could put their minds together and come up with a uniform loading requirement.
On the original diagram, it looks like you're checking moment in the ladder without considering the intermediate supports.
Required ladder load and safety factor will vary depending on the applicable codes- may be from OSHA, ASCE 7, etc.
I assume the two loads represent two climbers spaced out.
I could buy the (2) 250 lb loads as 2 climbers if they were spaced even 2 rungs apart, but dik's notes say that those are on adjacent rungs. Not saying that it couldn't be 2 climbers, but you'd really have to work at it to stack up like that.
I've been designing them wrong for years... A14.3 states:
It doesn't cause a problem because the loading doesn't impact the rungs or the side rails... but program fixed and notes revised... thanks.
Note Revised to... "1.2 1.1KN (250LB) AT ANY LOCATION ON ANY TWO ADJACENT A RUNGS IN ACCORD WITH ANSI A14.3;" I cannot edit the original posting.
I would interpret that note a little differently. Attachments are not rungs. See below.
Also, 1.2kN is 270LB, not 250.
BA
BART... I think you're correct and have adjusted my notes and program to suit. and load was changed to 1.1kN... thanks.