fixed and pinned supports
abdallah hamdan
36
if I have a beam with pin supports (columns) as in fig (1)
Is having a weight P due to the existence of upper floors on the beam sides as in fig 2, lead the beam to act as there is fixed support on both ends?
it would depend IMHO on the geometry of the beam and the attachment of the beam to the column.
if a uniform beam, then fixed ends are unconservative. If a variable section, then maybe assume fixed ends to size the ends and simply supported to size the mid-span.
if the end fastener pattern is capable of handling moment then foxed ends are reasonable, if not, then not.
thank you for your response, must the beam end always be designed as pinned supports be more conservative?
abdallah hamdan said:
...must the beam end always be designed as pinned supports be more conservative?
That will give the highest positive moment in the span, so it's conservative for that.
There could be some negative moment at the supports. If this is a concrete beam, then you'll need some reinforcing steel at the top to handle it. For example, in the ACI 318 Table 6.5.2, there are simplified expressions for bending moments. For the case of "Interior face of exterior support" and "member built integrally with supporting column," the negative moment would be Mu = wu Ln^2 / 16. Short of a detailed analysis, I would design the negative steel for at least this much.
so, what should I do, assign a fix or pin support at end of the beam?
or should I assign a partial fixity for beam ends that will give a reaction moment of "wu Ln^2 / 16" at beam ends
Wl/8 midspan, Wl/16 at supports. That should do it, unless the support is truly fixed, which is rare.
...so, what should I do, assign a fix or pin support at end of the beam?...
Short of a formal frame analysis, I recommend doing what hokie66 typed.
abdallah hamdan,
You are misusing the terms "pinned" and "fixed" supports. A pinned support permits free rotation but does not permit translation. A fixed support permits neither rotation nor translation.
The beam in your first diagram is best analyzed using a pin and roller support, if the beam is hinged to the column.
The beam in your second diagram is best analyzed using a rotational restraint at each end commensurate with the stiffness of the beam and columns. The load 'P' at each end contributes negligible rotational resistance, but if the beams and columns are rigidly connected together, the moment may be substantial.
The answer to your question depends on the stiffness of the members coming together at each joint. An analysis can be carried out to determine end moments on the beam. In some cases, you may wish to estimate the end moments based on experience or values permitted by code.
BA
If it's constructed, assuming a slab clamped in a stairshaft wall or elevator wall, I generally treat them as fixed end. If cast into a keyway in the wall then I treat it as pinned. If in a keyway, but at the corner of a wall, I treat the top reinforcing (only the top) as being fixed at that corner with whatever contributing moment I calculate.
BARetired has it right. In reality, building structures rarely have either purely fixed or purely pinned connections. I use 'rigid' for a connection which has a substantial amount of bending moment, and account for that rigidity in design, if not in analysis.
If I have 20 storeys of a concrete shaft coming down with a 6" or 8" slab 'pinched' between the walls, I would normally consider that as being pretty nearly a fixed conditon.
dik thats a part of my question, how many stories above are to consider it fixed, or is there any way to ensure the fixity of the support? by detailing maybe
I have been searching for 3 days and found that extending negative moment bars in a column by development length will develop fix joint between column and beam, but I don't know how many bars must be developed and have no clear vision about this detail
if not by detailing, can I calculate the (sum stiffness of column/sum stiffness of beam) ratio at the joint "a" (Ψa) and if it's very small I will consider it fixed support? isn't that a strong beam weak column situation?
I disagree with dik, and would always consider the connection of a floor slab to a core wall to be pinned...for the slab design. Some engineers would be less conservative, but the method of construction is likely to intervene. For example...if the core walls are slip formed as a result of a decision by the builder.
ok then, is there any detail to ensure a fixed joint or any calculation method?
Happens, I guess... in these environs, core walls are not generally slip formed and the slab is clamped between stories.
I have reached to point and I think it's true
these are details for fixed support based on "SP 34", and these are similar to the moment-resisting frame joint details
so if I want to assign fixed support between column and beam I will provide this details in the design, thanks all
Those are rigid joints, but not 'fixed'. The amount of rotation depends on the stiffness of the column.
I think some clarification is needed. The OP is referring to Fig. 7.14A of SP34, "Handbook on Concrete Reinforcing and Detailing" in which the term "FIXED" is used.
A beam may be fixed to a column, meaning that the beam and column are rigidly connected, hence have equal rotation. That does not mean the beam has a fixed support, because, as hokie66 pointed out, the joint will rotate when load is applied to the beam. The amount of rotation depends on the stiffness of all members meeting at the joint.
BA