Shear Wall Hardware Manufacturer Claims ACI 318 Anchorage Requirements Don't Apply 15

Status
Not open for further replies.

D.E.N.

Structural
Apr 22, 2021
31
0
6
US
TL;DR:
A shear wall hardware product manufacturer is claiming a steel threaded rod with epoxy anchored to concrete does not need to comply with ACI 318 anchorage provisions. I disagree. If ACI equations are used to check the anchor’s capacity, the product would have a reduced capacity and wouldn’t work as they have designed.

Full explanation:
I am the EOR on a large 5-story light-framed wood apartment building. I designed and detailed all of the shear walls using “typical” hardware, such as coil straps floor-to-floor and holdowns with threaded rods in epoxy at the base. Recently, I received a hardware substitution request from the GC, proposing a different product. Initially, I assumed this was a request to substitute hardware directly from a different manufacturer. However, the submittal proposes a completely different shear wall system.

The proposed system is a proprietary continuous hold-down assembly that connects to the building at the roof level only and anchors to the concrete at the bottom. Its tension capacity is based on testing and comes with a “code approval” report from a certified testing agency. This report, a Technical Evaluation Report (TER), is similar to an Evaluation Service Report (ESR) from other agencies. Due to the proprietary nature of the assembly, no published calculations or test result data are available; only a single allowable tension capacity is provided. The TER specifies installation conditions that must be followed to achieve the published tension capacity.

I have several concerns about this proposed system's ability to resist the required shear wall overturning forces and the proposed load path. Although I have been working with the manufacturer to address these concerns, one aspect of the design remains problematic. Both the manufacturer and the testing agency assert that the system's anchorage into the concrete does not need to be checked using ACI 318 anchorage provisions. The proposed shear wall system consists of a steel cable assembly with steel threaded rods at each end, with the bottom rod embedded in an epoxy-filled hole in the concrete. In my opinion, this anchorage design is not proprietary since it involves a steel threaded rod with epoxy in concrete, which is clearly defined in ACI 318. I would understand the argument if we were talking about a Simpson “LSTHD” Strap-Tie Holdown or MiTek “LSTAD” Foundation Strap, which is a truly proprietary anchorage design since it is just bent steel embedded in the concrete. But this is a steel threaded rod embedded in epoxy that just happens to be attached to the end of a proprietary cable assembly.

The manufacturer has a proprietary epoxy with an ESR report, stating to follow ACI 318-14 Chapter 17. However, the testing agency and manufacturer claim that the ESR for the epoxy is not valid when used with the cable hold-down system. They argue that the ESR only applies when the epoxy anchors steel threaded rods to concrete. It just so happens that the bottom of the cable hold-down system has a steel threaded rod attached to it…

Problem:
Using ACI 318 equations to check the anchorage capacity, I find that the assembly's allowable tension capacity is about 60% less than the manufacturer’s published values, primarily due to concrete breakout. This calculation includes product-specific variables and factors from ACI 355.4 tests, accounting for any proprietary epoxy behavior, which are published in the ESR.

I believe the proposed system’s anchorage must be checked using ACI 318 provisions, as the design closely matches the scenarios covered in the standard. The difference between the published assembly capacity and calculated anchorage capacity is a significant concern that I want to resolve before allowing the product to be used in my building. The testing agency and the manufacturer are telling me not to worry about it since the submittal and the TER are both sealed by PEs in the project state. They claim that since it is a delegated design, I don’t need to worry about how it interacts with my building. I would like to reject the entire system and stick with the original design, but the contractor really wants to use the cable system.

Question:
Have you ever dealt with something like this before? I don’t see how I can allow this anchorage “design” to bypass the ACI 318 requirements just because they are calling a standard anchorage method “proprietary.”
 
Replies continue below

Recommended for you

D.E.N., thanks for the update, and great job holding your ground on this.

The GC just informed me that the manufacturer agreed that they would not be able to provide what I asked for to approve their system
Yeah, I wonder why?!? Even they know their half-baked system doesn't actually meet code.
 
Not too surprising; they know there is no upside for them to run all these calcs. Lose 1 sale but waste a boatload of time to get to the same conclusion OP (and we) already know. Easier to just say nah we can't do it sorry.
 
The product is QuickTie, which was never directly mentioned (only visible in attachments). Now hopefully this thread appears in google searches.
 
EngDm said:
The product is QuickTie, which was never directly mentioned (only visible in attachments). Now hopefully this thread appears in google searches.

[tt]QuickTie[/tt]

QuickTie

QuickTie

Just helping out the algorithm [wink]
 
To be fair, I don't necessarily think this system can't work as intended, but it seems like they have an anchorage problem when it comes to adhesive anchors under long-term sustained tension. I feel like they could resolve this relatively easily with improved anchorage design.
 
bones - true, but then you have to consider compensation for shrinkage and cable relaxation, and it has to be automatic - once finishes are installed there will be no way to monitor or correct it.
 
What I mostly don't like is it seems you, the EOR, has to figure out the additional tension loading required to account for the relaxation due to shrinkage long term to provide adequate pre-tension. I don't feel like a simple "increase load by this amount" is sufficient for this as shrinkage isn't that straight forward for wood and can be too easily changed based on how you detail/design the wall and plates as well as lumber species.
 
I think the engineering challenge of reliably managing the loss of cable prestress is on par with the engineering challenge of prestressed concrete. I think it could be designed for with enough testing and validation, but that sample calc they provided seemed kind of hand-wavy and simplistic.
 