- Thread starter
- #101
GregLocock
Automotive
- Apr 10, 2001
- 23,434
The interconnectors are rated at 600 MW (roughly). It was when they bombed out due to overload that the system black cascade really got going. So any intermittency handler has to cope with a 600 MW draw. Mr Musk's Magic Machine gives a 10 minute breathing space. I don't know how long it takes to get a non spinning reserve up to 600 MW. What they should be doing is using the interconnector load as an indicator to bring in non spinning reserves, rather than relying on it running at 100% as it is a cheap source of baseload.
Cheers
Greg Locock