Copying specifications. I don't have a problem with this, why re-invent the wheel. What gets expensive is when someone copies a spec that they don't understand. If the engineer doesn't understand the spec he may use a spec for the wrong application.
We installed a standby generator for a prison years ago. The spec was copied from another government installation which was off the grid. There were a few other mistakes. We installed a 500 KW when a 200 KW or 225 KW would have done the job.
I always recommend buying the transfer switch with the genset. The pricing is usually excellent. You also get compatibility most of the time.
The set I have just finished installing had the transfer switch bought with the set. It isn't directly compatible with the set. The drawing shows the ATS sending a start signal to the genset with a pair of volt-free contacts.
The genset has a voltage monitoring board which starts the set on the failure of the mains. It also monitors the genset voltage and sends an "OK to transfer" signal to the genset contactor in the ATS when the genset voltage stabilizes.
The drawing showed both these contacts connected together.
The mains voltage monitoring circuit in the genset controls was not wired.
The ATS had provision for the "OK to transfer" signal but as stated the drawing showed the wires connected to the wrong terminals.
The as soon as the genset control was put in automatic, it would start and run continuously. With the input to the voltage monitor not wired, it thought the power had failled.
When the power did fail, the ATS would not put the load on the genset because the "OK to transfer" circuit was wired to the "Start genset" circuit. Two sets of volt free contacts wired to each other.
I called the contractor and had an electrician install a small breaker and run two more conductors between the ATS and the genset. Ignored the manufacturers drawing and connected things properly and all is working well now.
What's the point?
Stuff happens, that's life. If you understand how your systems work and there is a problem or mistake, you deal with it (often quickly, easily and economically) and move on.
It's working well now.
I spec'ed a single phase set about two years ago. I got a quote from my favorite supplier and the customer got his own quote. Much lower than my price so he went with the set he found.
Came time to install the set and it was smaller then quoted. The salesman knew that a three phase set could be used for single phase, but didn't know that it had to be derated 1/3.
I had a few interesting conversations with the salesman and he referred me to the service manager who, the salesman said, would send me the proper circuit breaker to get the full output from the set. The service manager confirmed, by e-mail, that the set size was as I had said and the rating was as I had said. I gave the e-mail to the customer and he went back to the sales department. The vendor gave him a cash refund for the difference in price between the size of the set quoted and the size of the set supplied. The customer was happy, we arranged a couple of air conditioners to run only on the mains and not on the generator, and I considered the final installation as not perfect but pretty good.
My customer is happy with me and with the vendor and we will both be happy to deal with this vendor in the future.
respectfully