Mbrooke
Electrical
- Nov 12, 2012
- 2,546
Does anyone know the 30*C AC resistance (or impedance) of 14, 12 and 10 gauge wire?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
You will never know the source impedance with a sufficient degree of accuracy for any of those to ever matter.
David Beach said:You will never know the source impedance with a sufficient degree of accuracy for any of those to ever matter.
Waross said:It is pretty obvious that you do not have a copy of the code that includes Table 68.short circuit interrupting.
And as sad as the situation with the CSA may be, what on earth does that controversy have to do with the coefficient of resistance between 30 degrees and 75 degrees?
By the way, given the difference between the DC resistance and the effective AC resistance, does the temperature coefficient of a copper wire apply to the effective AC resistance or to just the DC component of the effective AC resistance.
oops. Back to the spread sheet.
Waross said:If you read the code you would know that Table 68 has to do with maximum allowable voltage drop on residential lighting circuits.
The voltage drop percentages are stated in the code, but table 68 lists maximum circuit lengths despite calculations and only for evenly distributed loading.
Your uninformed hubris is becoming onerous.
I have experienced 15 Amp circuits in conduit that were unable to trip magnetically on a dead short circuit, line to line.
What David Beach said, things change in the real world.
With all your worry about 75C vs 20C vs 30C vs 60c, have you paused to consider that a cooler wire, with less resistance is better able to cause an instantaneous trip.
In 99% of cases, the lower resistance is in your favour.
After dissing my suggestion that interrupting ratings are often conservative, you may consider researching the range of X/R ratios of distribution transformers and look up the assumed X/R ratings that interrupting ratings are based on.
All of your agonizing will be for naught if the transformer has an unusually high X/R ratio.
Interrupting ratings are based on an assumed X/R rating and if an unusual transformer has a higher than assumed X/R ratio, the fault current will be above the calculated interrupting rating.
Conversely, the fault current from a transformer with a lower than assumed X/R rating will be lower than assumed.