Where does this compression come from? If the mainspan is supposed to be a stand alone structure and was simply set on the pylon, it can have no free forces to create external compression. The compression of 11 is supposed to be resisted internally, but has failed. The backspan is cast in place so the wet concrete will not create free forces. Removing falsework would load 14 in compression but in my mind intelligent design would have that force resisted internally also. When the thing fails, of course you reach for anything.
Since node 11/12 was failing, how much capacity is left? (Assuming you get there before it colllapses).
Anything relied on would have been an assumption. FIGG advanced an idea to restrain (capture) 11/12 with channels extending to 9/10 at the deck level. We will never know if they intended those tiebacks to be temporary. Then they said the backspan would do the job so it appears they intended the ties to be temporary.
Here is a previous post:
Vance Wiley (Structural)18 Jun 19 18:27
Quote:
saikee119 (Structural)18 Jun 19 17:23 quoting "The fact the bridge collapsed before FIGG’s strengthening scheme could be devised is a good testimony on the technical competency of FIGG on the matter."
"Being sarcastic, right?
I still question this statement/position by FIGG: "Such restraint would of course be provided by the erection of the side span had the bridge been able to achieve completion. "
Could someone identify the elements/parts in the closure strip over the Pylon which will provide 2000 kips of tension tie between the north and main {deck ?}."