Phil1934 - 181 Fremont is an interesting building, in that it is intended to be earthquake "resilient". That is, it is designed to such a high standard that it is suppose to remain functional & occupied, post earthquake. It is also highly instrumented.
hamjohn - Carl Chan makes some interesting points and he obviously spent as much if not more time researching both the TJPA & 301 Mission as I have. He makes an interesting point about the bracing for the podium excavation. Namely that the upper bracing is fixed to the tower, whereas the two lower tiers of bracing are fixed to the shoring wall below the tower. This certainly provides for the upper bracing & the lower bracing to behave differently.
As extensive as his research was, he may have missed the early tests done on timber pile extraction and settlement. The old Transbay Terminal adjacent to the Millennium Tower had an 11 to 13 foot deep basement. Demolition of the old terminal would not have represented any great change to the soil beneath the terminal. More so because it was incrementally demolished and back-filled almost to street level.
Testing:
With ground cleared of the old terminal debris - on the west end of the TJPA, they tested a number of CDSM shoring shoring wall schemes, while on the east end (Zone 4) aka Millennium Tower zone, they performed a timber pile extraction & ground effect test. An area of piles was select and ground elevations recorded & instrumented, then a 30ft to 40ft pile was extracted and areal ground subsidence recorded. They also performed this test while quickly following up with tremie placed @50psi bentonite/concrete. I believe the method chosen for removing the timber piles was that piles could only be removed one at a time and the hole filled with tremie concrete before the adjacent pile could be extracted. When the pile extractions were done adjacent to structures with shallow basements/footing or other sensitive criteria, they vibrated casings in place, extracted the piles, filled the casing with concrete & extracted the casing (one at a time). Indeed, this casing method was used on 3 timber piles adjacent to the buried old PG&E Vault
between the TJPA & Millennium Tower before the CDSM shoring wall was placed.
In Carl Chan's Millennium Tower Supplement, he identifies an area beneath the tower as an "abandoned shoring wall" this is actually the 25ft(wide) x 3 ft (thick) Cantilever Slab that extends off the south end of the tower foundation & flies over the older PG&E Utility Vault that remains buried between the tower & the TJPA.
It is confusing because an identical PG&E vault was built directly over this one, in the basement of the tower on level B1. From the end of the southern end of the tower foundation a section of ~grade beam~ is incorporated into the foundation to accommodate the innermost corner brace. There are drawings showing the shoring wall stepping up to fill the space below the 3 ft cantilever slab.
The time period in the fall of 2010, that Carl Chan denotes as a period where the tower ceased to sink is actually noted by Arup as a time when the tower briefly began to settle back in the opposite direction and can be seen in the contour .gif posted above and identified by this signature slide. This is when the tower returns to its north-west settlement.
It takes place early in the TJPA's monitoring of the tower at a time when they were recording every 30 to 60 days. The tower most definitely had not stopped shifting. About the time the tower returned to its West-North-Westerly tilt there is an anecdote that an occupant in the tower heard a loud bang and felt the building shake. Perhaps this is when cracks developed in the north-west corner on levels 4 & 5 of the parking structure. This corner also represents where Webcor Bldrs. had water intrusion problems, as shown in the photo (fig. 3, pg. 3) in Carl Chan's Millennium Tower Supplement. It is worth noting that the transition zones in the different soil layers are punctuated by crust layers that can yield more resistance that the the same soil layer below the transition. The depth of the crust layers are fairly easy to identify in the 4 indicator pile tests found in the files the city has provided during the Oversight Committee hearings. There was concern about penetrating the crust layer as the pile capacity could drop.
Returning to Carl Chan's observation of the podium excavation shoring, one has to wonder how much stress the bracing was under. It appears that every panel of the entire east CDSM shoring wall showed signs of distress, as evidenced by the degree of water intrusion. Meanwhile there is virtually no water intrusion on the shoring wall beneath the tower.
East Shoring Wall:
North Shoring Wall:
South Shoring Wall:
When one goes looking for an outside groundwater influence that may have accelerated the sinking of the tower, one has to look at the work that took place at 350 Mission St.(Webcor Bldrs.), before looking to the TJPA. 350 Mission St. began dewatering in May of 2013. They certainly didn't install a CDSM shoring wall 105ft deep into Old Bay Clay like the TJPA. While the TJPA started dewatering in Zone 4 shortly after 350 Mission, just how much "Areal Effect" could this dewatering have with a CDSM shoring wall 105ft deep into Old Bay Clay backed up by a 7ft thick secant buttress wall drilled 260ft down & socketed 10ft into bedrock.
350 Mission End of April:
TJPA Zone 4 - Aug 10 2013
The specification for water draw down outside the TJPA excavation was -3ft based on established piezometer readings, the dewatering contractor was required to recharge the groundwater if the levels dropped below -3ft. The big "IF" is whether this was adhered to.
Dewatering:
Window Update:
Permits were issued to remove wall & window sill materials in units 35B, 36B & 37B to inspect the curtain wall. The earlier Fire-Stop problem was in 31B and
is at the same vertical building line. The section of floor slab is between the two sets of SMRF's which are slightly offset, accounting for the recess in the building facade. The Window offset is immediately adjacent to the east inner SMRF.
Reinforcing the External Pane of 36B
There have also been problems at street level. The sidewalk in this area has been opened up, excavated & replaced. The towers external fire hose connections are located at the base of tower at this building line. There is also a water spigot that has a history of leaking. The HOA in 2016 commissioned the installation of geotechnical instrumentation in the sidewalk in this location.
Remediation Study:
A permit has JUST been filed to drill two soil exploration borings to 250 feet deep, the name on the application is Ron Hamburger. This is to be done from the top of the Mat Foundation, presumably from the basement.