I think this is what is seen beyond the North end of the bridge before collapse. It defies gravity far too long.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
dik said:engibeer: When something may be in a state of impending collapse... changing the load regime at any location may not be a really good idea <G>.
Dik
Close enough.Ingenuity said:For member #11 with 2 each x 1-3/4" PT bars on a 24" x 21" concrete cross section, with PT bars stressed to about 70% of UTS - that is about 540 kips over about 500 in2 of concrete - so about 1,000 psi of axial compressive stress. Self weight support reaction of 950 kips and a member #11 angle of 36o equates to a compressive force of about 1600 kips (3,100 psi axial compressive stress) - add the self weight force to the stress induced by the PT to member #11 and you get a net of about 2,140 kips (or 4,100 psi axial compressive stress). IF (big IF) there was a 10% overstress to PT bars that would only increase the force (and stress) by 54 kips (100 psi) to the cross section, for a total of about 2,200 kips (4,400 psi).
2,200 kips is not "okay" for member #11. Far from it.Ingenuity said:For 8,000+ psi concrete, adequately reinforced with mild steel reinforcing, (including significant confinement reinforcement) and the level of stress to the member should be okay...
PeterDow said:Newbie here.
Peter Dowe said:This tells us that only calculating with a risky safety factor of only 1.2 can we assess that the truss member #11 is just barely strong enough to hold the bridge up with no additional load from post-tensioning bars or from any pedestrians on the bridge. Using anything more cautious for a design safety factor would warn that the bridge is at an unacceptable risk of coming down.
Peter Dowe said:Of course it would be much worse if there were any issues with the concrete not being as specified.
Peter Dowe said:member #11 is just barely strong enough to hold the bridge up with no additional load from post-tensioning bars
I'll recheck about PT rods as something on my working drawings not fit.3DDave (Aerospace) said:old_jim, there is already evidence that the tendons are intact; therefore there was no shock load.
Thanks!bobwhite said:Peter Dow is accurate with the equation with the design axial force.
bobwhite said:Peter Dow is accurate with the equation except that the design axial force using his assumed reinforcement is about 2178 kips, f'c = 8500, 10-#7 fy = 60000 longitudinal bars equivalent to 6 sq in 1.19% of Ag.
Not a slope more like my force vector diagram's 1v:1.4h?bobwhite said:Diagonal #11 has a slope of about 1v:1.6h
If your slope is wrong you will miscalculate the force too.bobwhite said:This results in an unfactored dead load force = 1812 kips based on the truss end reaction of 950 kips.
So "about 1600 kips" is right for the compression force on member #11 from the bridge dead load too, I agree.Ingenuity said:Self weight support reaction of 950 kips and a member #11 angle of 36o equates to a compressive force of about 1600 kips
Agreed.bobwhite said:Diagonal #11 has a slope of about 1v:1.38h based on the prelim drawings.
Agreed.bobwhite said:This results in an unfactored dead load force = 1619 kips based on the truss end reaction of 950 kips.
waross said:I wonder if the upper PT rod in member 11 was removed after it was relieved. Is it visible in any of the pictures?
bobwhite said:I tend to agree with ingenuity that the failure occurred at the top of diagonal #11 and #10 in the canopy slab at least based on what the video shows.